When applying the derate to conductors based on the number of current carrying conductors in a raceway I know you can use the 90 degree column if using THHN.  I understand all of that.  This does not effect the sizing of the overcurrent device correct?  If your load requires a 20 amp circuit then a 20amp circuit it is, but after derating you might have to use a #10 thhn conductor.  Am I understanding this correctly?
	
		
			
		
		
	
				
			
				