#4 is a good break point.
anything larger, it's aluminum, with a couple caveats:
first, i won't use anything other than simpull, by southwire.
i got snookered on the last job into trying someone else's
flavor of simpull. i'll never do that again. ever. lotta long feeders
in pvc underground.... used 40 gallons of lube, and almost broke
the pull rope on the first pull, which was 700' long or so, and i started
it dry. what a nightmare. the wire was cerro. never again.
ilsco lugs, butt splices, etc. done with the specific die, not a ranging die
or dieless. no setscrew lugs, ever. where i have to hit a breaker or setscrew
lug, i use ilsco offset finger lugs, with the panduit heat shrink.
no chinese lugs. i've had them split.
for bolted connections, grade 8 3/8-24 allen head cap screws, washers, and nylocks.
you can torque them to 37 ft. lbs. you could use 1/2", but the lug material is starting
to flow at 37, so it seems overkill. on the last piece of switchgear i made up, i had
two "grade 5" bolts twist off at around 15 ft lbs.
on top of that, panduit 600 volt direct burial listed self vulcanizing heat shrink,
on lugs and butt splices, and finger lugs. no exceptions.
you end up with a hermetically sealed connection.
it's as good a means as copper, and it's running 22% of the price of copper.
this is tomorrows pull... i have seven pulls to make that will eat most of this up.
the difference in price between this and copper is about $75,000. hard to justify it.