petersonra

Senior Member
Location
Northern illinois
Occupation
Semi-retired engineer
UL508a allows unevaluated components to be used if they are on a GFCI (along with some other requirements that don't matter for this question).

The standard says this.

B2.2.3 The secondary circuit shall be protected by a Class A (6 mA trip) circuit breaker and ground-fault
circuit-interrupter (CBGFCI), or a Class A receptacle-type ground-fault circuit-interrupter (GFCI) complying
with the Standard for Ground-Fault Circuit-Interrupters, UL 943, and used within its ratings.

Does a blind GFCI meet the requirement that it be a receptacle type GFCI?

I am thinking not.
 
If you use a blind GFCI, rated at 6ma, to protect a receptacle or receptacles, what requirement isn't being met here? CB protection is another thing entirely, and would depend on the ampacity of the conductors and the receptacle ratings.

Perhaps run it by your UL508a inspector, as I hear some can be unnecessarily picky, but I'd argue that the intent of protection is being met here.



SceneryDriver
 
That is one of the main purposes for those blind GFCIs, I used them all of the time for the unevaluated components issue. I never once had a UL inspector even bring it up in a conversation.


Sent from my iPhone using Tapatalk
 
That is one of the main purposes for those blind GFCIs, I used them all of the time for the unevaluated components issue. I never once had a UL inspector even bring it up in a conversation.


Sent from my iPhone using Tapatalk

I have seen it done that way too.
 
B2.2.3 The secondary circuit shall be protected by a Class A (6 mA trip) circuit breaker and ground-fault
circuit-interrupter (CBGFCI), or a Class A receptacle-type ground-fault circuit-interrupter (GFCI) complying
with the Standard for Ground-Fault Circuit-Interrupters, UL 943, and used within its ratings. For a
receptacle-type GFCI, the following additional requirements apply:
a) The component shall be connected directly to the terminals (not plugged into the receptacle);
b) A marking on or adjacent to the receptacle shall indicate the receptacle is not to be used for
external connections; and
c) The receptacle shall be mounted so that it is not accessible from outside the enclosure.

I was going to call UL and ask but I never got around to it. It sure seems from the full context of the provision that they expect a receptacle that can have something plugged into is going to be used.
 
I agree with the others. I can't imagine why the dead front gfci would not meet the requirement for gfci protection. I assume by blind GFCI you also mean dead front.
 