corvalan
Situation:
10 feet tap rule ending on a single instantaneous trip over current protection device.
Details:
1: Ampacity of the No. 1/0 AWG tap conductor (150 A) is more than 1/10 the ampere rating (1,200 A) of the upstream OCPD.
2: The tap conductor is physically well protected.
3: The tap conductor doesn't leave the enclosure where it arrives.
4: The tap conductor terminates on an enclosure with an ampere rating less than the ampacity of the tap conductor.
5: The tap conductor terminates on an instantaneous trip breaker (ITB). The ITB has only magnetic trip. The enclosure where this ITB is installed is listed motor combination starter enclosure. The nominal ampere rating of this ITB is 250 A and its pick-up is set to 600A.
6: The motor size protected by the ITB is 50HP @ 460V with a FLA of 65 A. Therefore the ITB is properly sized for this motor.
Question:
1: Is this tap conductor properly applied according to the NEC?
1.a) Which ampere rating should be the tap conductor be applied, the nominal 250 A or the actual PU amps determined by the settings of the ITB (600 A)?
1.b): If the ampere rating to be compared is not the nominal ampere rating of the ITB (250 A) but the actual PU of 600 A, then then 240.21 (B)(5) is not satisfied. If that is the case, it appears to me that this 10 foot tap rule will never be able to be applied to a set of combination starters fed by a gutter.
Details:
Question: