Tap terminating on a listed combination starter
240.4(E)(6) seems superfluous to me, I don't know what the thinking was.
240.4(E)(3) directs you to 240.21, and 240.21(F) directs you to 430.28 and 430.53 for motor feeders and motor branch circuits.
Why the specific reference to 430.53(D) when there is already a reference to 430.53 in its entirety.
240.21(F) covers both motor feeder [430.28] and branch [430.53] circuits... which seem to put us back to 430.53(D) for a single motor... and thus the reason for 240.4(E)(6). Keep in mind a motor branch circuit can supply more than one motor.
I don't see it. As you say, 240.21(F) covers both motor feeder and branch circuits. 240.4(E)(6) covers a specific motor branch circuit that is already covered by 240.21(F).
Or in other words, 430.53(D) is a part of 430.53 which is referenced in 240.21(F). 240.4(E)(6) is redundant.
I agree with you on that part. On the other hand I see 240.4(E)(6) as a direct entry compared to the beat-around-the-bush entry of (E)(3).
What if transformer secondary tap to instantaneous breaker set at "1"
I too have a similar situation (but different!). Should I post this as a new thread?
In my situation I have a 500 kVA, 480V transformer, less than 10' feet away and supplying a 600 amp (frame) instantaneous only (electronic!) breaker that is (let's assume) part of a listed combination controller. (Actually its a VFD). The transformer has NO secondary protection.
What I think is interesting (significant) is that the (electronic!) instantaneous breaker of the starter has an adjustment setting of "1" (i.e. a vertical line at 600amps on the current-time curve). My understanding is that being electronic it's not relying on magnetic forces of an "instantaneous" current.
Can I use this setting of "1" (600amps) to protect my 620amps worth of transformer secondary tap conductors? If set to "1", doesn't this provide the same protection as a electronic breaker with long time, short time, inverse time capabilities (i.e a breaker analogous to a thermal-magnetic breaker)? Is 240.21.(C)(2) fulfilled?