As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.[/QUOTE]
I sure hope you're not talking about the back stab ones I'm continually finding problems with!
I'm guessing 99.9% of those failures were where the receptacle was used as a feed through device or had a heave load connected?
I have never done much service work but have run across more screw connection failures than back wiring failures. Most of the failures were receptacles used as feed through devices or had a heavy load (space heater) connected.
All of the projects I work on get back wired but always pigtailed. In the 31+ years I have been in business I have never had a call back from a failed connection.
If there were no problems why did UL change the rules to prohibit using the back stab connections with #12 wire?As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.
Because if the receptacles are originally back-stabbed with #12 and then removed and re-used and back-stabbed with #14 this led to failures due to the contact points not grabbing the smaller wire tight enough.If there were no problems why did UL change the rules to prohibit using the back stab connections with #12 wire?
If the device is manufactured with pressure plate type connecting, ( as in spec grade and HG type receptacles) back wiring is the better choice IMO.
OOOOOh I hate those. I prefer a regular screw any day. Those clamp type garbage connectors come loose as you fold back the wires with 12 ga.
Roger
Roger
Yes, where they were installed correctly. I too have seen more problems with screw connections than back stab.I seriously doubt that was the reasoning, However I was not active in the process at that time. My understanding is that for feed through the back stab cannot handle the load.
Because there werre plenty of failures. I have never seen a feed through fail when using the screws where they were installed correctly. However place a space heater on a backstab and you will have a failure. Just a mater of time.
Where did you come up with that quote?
Roger
Probably poor installation technique.So can you quantify those screw connections as failing overall, or due to poor original installation technique?
You just may be following a crew or even a whole company that just didn't care what happened after their check cleared.
Can you cite a source for that comment?Because if the receptacles are originally back-stabbed with #12 and then removed and re-used and back-stabbed with #14 this led to failures due to the contact points not grabbing the smaller wire tight enough.
Personally I see more backstab than screw connection failures, however have run across groups of screw connection failures, seem to be related to torque setting on original installer's cordless. Or obviously sloppy loops.Yes, where they were installed correctly. I too have seen more problems with screw connections than back stab.