JDB3
- San Antonio, Texas
I sure am glad
that the NEC makes all of this as clear as "mud" !!:jawdrop:
I sure am gladthat the NEC makes all of this as clear as "mud" !!:jawdrop:
Exactly why I added:"(I did say most, there are occasional exceptions)":happyyes:}}} GFCI is kind of simpler then it once was as well. If outdoors or within 6 feet of a sink there isn't much to question anymore, plus in most any space with concrete or dirt for a floor in/at a dwelling (I did say most, there are occasional exceptions) . Dwelling kitchens only slightly more complicated when it comes to GFCI, plus all bath receptacles. {{{
Need to kind-of watch, talking about concrete floor in a dwelling. Some of the houses (dwellings) that I do, have a stained floor in them. Some of these are 3,200 square feet or so & rather nice custom homes.
Because the AFCI manufacturers spent a lot of time and $$$ to get a non perfected product as a required item into the NEC in the first place:roll:I will never understand this. Why cant CMP just say all 120 volts 15 and 20 amp circuits within a dwelling shall have 30ma ground fault protection and leave it at that? Same fire protection without guess work or nuisance tripping.
Opinions are like xxxxxxxx's , everyones got one it seems.Because the AFCI manufacturers spent a lot of time and $$$ to get a non perfected product as a required item into the NEC in the first place:roll:
And my opinion of AFCI's, as one who is forced to install them and deal with the related headaches rather than one who sells them, is they suck.Opinions are like xxxxxxxx's , everyones got one it seems.
ok I went over 15 minutes had laundry working real simple after I typed a long addition. 210.8 fig 210.44 states outlets supplying dishwashers need gfci but receptacles don't?????. the authors comment states that receptacles that serve dishwashers don't require GFCI. Anybody have the NEC handbook and MIKE HOLTS BOOK that can give an educated opinion on this
Thanx
Be safe
The handbook is wrong on this issue...I think they simply forgot to update the comment to reflect the 2014 code change.ok that is what I was leading to it states within "arc measurement" not just 6 ft. but also the authors comment stated no gfi needed for recpts. for built in dishwashers. this is under 210.8 6. now the illustration in 210.11 is listed fig. 210-44 referencing 210.8 d but says dwelling and states outlets supplying dishwashers must be gfci. Im not trying to defend an install, but really want to substantiate the handbook. Im not trying to cause controversy but is there something in here we are all missing. I know an arc of a circle is on a horizontal plane, regarding countertop placement, so this wording would mean that under cabinets wouldn't be included. Thanx for replying let me know what you think.
Would be nice to know who "proof reads" the NEC? Just a comment, cause stuff like this leads to problems.
FYI- I don't directly sell (I, like you, indirectly install and sell as you do) or manufacturer AFCI's...lol....an I have installed quite a few of them in my time with no issues to speak about.And my opinion of AFCI's, as one who is forced to install them and deal with the related headaches rather than one who sells them, is they suck.
Someone sitting on the other side of the table I'm sure sees it differently.
FYI- The NEC Handbook is not the NEC. It has content from the NEC in it...with added commentary.Would be nice to know who "proof reads" the NEC? Just a comment, cause stuff like this leads to problems.
I have not installed very many, only about fifty or so.FYI- I don't directly sell (I, like you, indirectly install and sell as you do) or manufacturer AFCI's...lol....an I have installed quite a few of them in my time with no issues to speak about.
When they first came out I had a really good run as a AFCI demon exorcist. Every time I would troubleshoot an AFCI problem it was a wiring error that was the problem. Go to the biggest three or four gang switch box in the house and find where the neutrals from multiple circuits were jammed under one wire nut, sniff out that mis-wired breaker in the panel, find the recept with the bare EGC just barely touching the silver screw, etc...
I had hundreds of conversations at the local supply houses and electrician watering holes defending AFCI's. "They are fine, you guys just don't know how to wire a circuit", I would say. "GFCI's had issues, they got better." I would say.
Then the day came when I got a call to fix a troublesome circuit on a house that I had wired. "How come when I turn on my TV sometimes the power goes out?" asked the HO.
"I don't know. I'll come check it out" I said.
Checked the circuit from head to toe and it was clean. Talked to the tech guy at GE, "Yes, there are some problems with those breakers, I'll send you a new better one right now, no charge."
That is when the penny dropped. THOSE ROTTEN SOB'S REALLY ARE SELLING SOMETHING THAT THEY KNOW DOES NOT WORK. I switched from an AFCI defender to an AFCI hater that instant.
Nope. Not so. I had a similar problem with a SQ D breaker. I started a thread about that one. And I will repeat for clarity, I was late jumping on the anti AFCI bandwagon. I defended them for about ten years.lol...and with one incident you threw the baby out with the bath water. You lumped all manufacturers in that proverbial "SCUM" syndrome...lol.....
Really? What about this guy? http://www.combinationafci.com/Not a single person can say AFCI's do not do what they intended to do. ...
Well I am one who did investigate and I can say with 100% certainty that the problem was the AFCI breaker. Two different brands SQ D HO and GE THQ. Both times it was the breaker. No doubt, no alternate answer, no question about it, no stone left unturned.When I question those who had bad experienced with AFCI's i magically get very little details and they hardly ever say they actually "investigated" the issue and with 100% certainty contributed the issue to the AFCI....
Mike Holt had to embarrassingly retract his original statements about AFCI's.....and the Mr. Engle propaganda that is posted is just someone with sour grapes over their fallout with a company to which they were employed and pushed AFCI's for years....Nope. Not so. I had a similar problem with a SQ D breaker. I started a thread about that one. And I will repeat for clarity, I was late jumping on the anti AFCI bandwagon. I defended them for about ten years.
Mike Holt even put out a newsletter.http://www.mikeholt.com/newsletters.php?action=display&letterID=1135