Not just the terminals. For instance you could have a 90C terminal but if the equipment (panelboard, e.g.)is rated 75C then you must use 75CEven if the code allowed it, the terminations at the OCPD would also need to be rated for 90?
If our electrician were to install 90deg. lugs on a 75deg. machine switch, would I then be able to use a smaller size wire? One that is rated in amps for 90deg. I know, trying to circumvent the code. I am just trying to save a little coin.
You answered yes, but your additional comment says no to the question askedYes. Use the 90C wire at its 75 C. or 60C rating.
A 90C wire has higher ampacity at 75C rating thanYou answered yes, but your additional comment says no to the question asked
A lot of equipment uses 90 deg lugs, but the entire assembly still only has a 75 deg rating (or 60).
A 90C wire has higher ampacity at 75C rating than
a 75C wire but smaller and so cheaper.
A 90? and 75? wire operating at the same level of current will be the same temperature where all other conditions are identical. Insulation rating has no bearing on terminal temperature limits.A 90C wire has higher ampacity at 75C rating than
a 75C wire but smaller and so cheaper.
A 90C wire has higher ampacity at 75C rating than
a 75C wire but smaller and so cheaper.
If our electrician were to install 90deg. lugs on a 75deg. machine switch, would I then be able to use a smaller size wire? One that is rated in amps for 90deg. I know, trying to circumvent the code. I am just trying to save a little coin.
And the only way to change the terminal rating would be to change the breaker.You also have to size per circuit breaker terminal ratings, so wouldn't you would have to change breaker terminals also if they aren't rated 90 degree.