If you were running 3-1/C #1/0 or larger on strut would you support the 3 conductors under one strut clamp or 3 separate strut clamps at each location? How is it most often done? Thanks.
You need a single clamp if the clamps and the strut are made of ferrous metal.If you were running 3-1/C #1/0 or larger on strut would you support the 3 conductors under one strut clamp or 3 separate strut clamps at each location? How is it most often done? Thanks.
You need a single clamp if the clamps and the strut are made of ferrous metal.
Single containing the 3 conductors or single for each ?
3 conductors w/ one clamp or kindorf strap. You might use a radiator type hose clamp between the supports to hold the bundle of 3 conductors together.
From the nature of your questions it sounds like you've never installed this stuff before.
It might really be in your interest to just read Article 332 so you can be sure you've got the basic requirements of your installation covered.
Wow...that must have cost a fortune..
I agree.
It was a large hospital, I was in there doing other electrical work and saw this MI work that was just getting finished up. These cables ran all over the hospital up and down floors and through finished suspended ceilings in a 24/7 facility. It had to be a very tough job to make it happen.