Hello all,
This is an updated and I think corrected idea for checking over.
Thank you!!
Two 3 phase 480 Volt machines- (50Amp air compressor and 13Amp air dryer)
I intend to wire 2 machines from a single 100Amp breaker.
I will go from panel about 2 feet into a small wire way (4x4x24" troffer) with #3 AWG CU. I will use Polaris 3 position connectors and splice two taps to each conductor. #10 AWG CU and #4 are the tap sizes.
The taps will be no more than 3 feel long and will terminate in fused discos with 70Amp and 15Amp current limiting RK1 fusees (MOCPD per nameplates.) (The 100 Amp circuit breaker has a max AIC rating of 34K, the fuse charts show way under 10K of let through at 40K value.)
#8 AWG CU will be used for grounding/ bonding from panel to both disconnects.
On the load side of the disconnects-
Circuit wiring will be reduced to #12 with #12 ground for the 15 Amp machine and #6 with #10 ground for the 50 Amp machine (both runs to machines are less than 20 feet)
All EMT will be bonded for circuits over 151 Volts.
Thank you for the input!!
This is an updated and I think corrected idea for checking over.
Thank you!!
Two 3 phase 480 Volt machines- (50Amp air compressor and 13Amp air dryer)
I intend to wire 2 machines from a single 100Amp breaker.
I will go from panel about 2 feet into a small wire way (4x4x24" troffer) with #3 AWG CU. I will use Polaris 3 position connectors and splice two taps to each conductor. #10 AWG CU and #4 are the tap sizes.
The taps will be no more than 3 feel long and will terminate in fused discos with 70Amp and 15Amp current limiting RK1 fusees (MOCPD per nameplates.) (The 100 Amp circuit breaker has a max AIC rating of 34K, the fuse charts show way under 10K of let through at 40K value.)
#8 AWG CU will be used for grounding/ bonding from panel to both disconnects.
On the load side of the disconnects-
Circuit wiring will be reduced to #12 with #12 ground for the 15 Amp machine and #6 with #10 ground for the 50 Amp machine (both runs to machines are less than 20 feet)
All EMT will be bonded for circuits over 151 Volts.
Thank you for the input!!