50% says YES, AWG 4 THHN can be use as a feeder for a 100 amps sub-panel and 50% says NO for a separated garage/shop. I am in doubt, but I would like to use it as I have a full spool and I am donating it.
Use it with a 90A breaker and you will be just fine. Unless there is a serious growing operation going on in the garage the main will never trip.50% says YES, AWG 4 THHN can be use as a feeder for a 100 amps sub-panel and 50% says NO for a separated garage/shop. I am in doubt, but I would like to use it as I have a full spool and I am donating it.
You can still use the 100A panel with the #4 and I'll bet a hundred dollars you will be fine with a 60A breaker.Thanks! I don't know why I still listening to all those "opinionated individuals" outside the forum. Maybe it is my fault as I was trying hard to use a 100 amps panel and a spool of #4 that I have in stock because a 90 amps breakers are too expensive. Mea Culpa!
Maybe do a load calculation and see if I can install in the same box and in the main panel a 60 amps breakers and run this existing #4. Uggg
Happy Easter! ... Too late?
You only need the 90 at the supply end of the feeder. The one at the garage panel can be any size.I paid $40.00 for this load center including the 100 breaker and I have in stock an extra 100 for the main panel. If I have to buy two 90s it will be too expensive, but I have extra 60s, so I will do the load and see if 60 will be enough.
... Should the 100 be in the main and the 90 in the garage
If I can go with 60 (after load calculation) I can install a 60 breaker with the same #4 and the 100 sub-panel and it will be ready for future expansion. Thanks
Sorry, it makes sense. If I can go with 60 (after load calculation) I can install a 60 breaker with the same #4 and the 100 sub-panel and it will be ready for future expansion. Thanks