Carultch
Senior Member
- Location
- Massachusetts
I would like to add that it is not just the termination that needs to be rated 75C, I believe many panel lugs are 90C rated, but the equipment must be rated 75C. The 90C lugs in my example will not help if the equipment is not rated 90C and it won't be.
In my example above, is it required that the 90C splices be accomplished in separate enclosures?
Or could I use a Polaris Insultap within the gutter space of a 75C rated panelboard or disconnect, and take credit for the Insultap's 90C rating?
Because the insultap is not a manufactured part of manufactured product. It is a field-installed connector.