mikeybmdb32
So, I know that the tables for NFPA 70E cannot be used if the exact parameters are not met (ie working distance, fault clearing time, max short ckt current, etc). However, I'm confused as to what the meaning of maximum fault clearing time means. Does it mean:
1) the actual maximum time that the upstream device could take to open. This would include the overload regions of the breaker curve and would almost never meet the table requirements.
2) the upstream device's operating time at the maximum short circuit current listed in the table?
3) the upstream device's operating time at the actual short circuit current of the equipment being worked on?
4) something else?
As always, thanks.
4) something else?
As always, thanks.