wbdvt
Senior Member
- Location
- Rutland, VT, USA
- Occupation
- Electrical Engineer, PE
I just don't see where it indicates in NFPA 70E_2015 that the actual bolted fault current and clearing time is required to use Table 130.7(C)(15)(A)(b). It does says, "The estimated maximum available short-circuit current, maximum fault-clearing times, and minimum working distances for various ac equipment types or classifications are listed in Table 130.7(C)(15)(A)(b)." It then lists the scenarios where you cannot use the table. I can tell you that when the actual bolted fault current from the utility is unknown, an infinite bus is often used. As I said before, when you get down to the lower voltage buses (ie 240 & 120) from an medium voltage service, the actual bolted fault current is not much different than an infinite bus.
Ok, I am traveling so I don't have my NFPA 70E copy with me but consider this:
Your actual bolted fault current is less than the maximum bolted fault current as shown in the tables but the clearing time is much higher due to the actual fault current being less than the maximum bolted fault current you decide to use based on an infinite bus. This puts you outside the parameters of the table. You have an employee working in PPE you said was acceptable based on your interpretation of the table parameters. There is an accident and the employee has less than the necessary PPE for the actual incident energy. He/She is severely injured. You are now on the witness stand with a lawyer (and they have been attending seminars on Arc Flash) who is questioning you on your decision. Will you be able to defend your decision on use of maximum available fault current from an infinite bus versus maximum available fault current able to be delivered by the utility?
Your call.