tonype
- New Jersey
Some people will spend far more time and effort to avoid doing things correctly that it would take to simply do it correctly in the first place.
Sure you don't want to go for 8"?![]()
Too bad it's a violation. Don't know the article, but it should be supported within 4" of a single gang box.
Even if this was less than 8", is the wrap around OK?
It's not code compliant as shown in the photo since it's not connected to the stud with a staple, strap or some other approved method.
Nothing in the code about wrap. Workman like manor on the other hand.
Well the AHJ could approve it but I don't see that happening.
334.30 Securing and Supporting. Nonmetallic-sheathed
cable shall be supported and secured by staples, cable ties,
straps, hangers, or similar fittings designed and installed so
as not to damage the cable, at intervals not exceeding 1.4 m
(4 1 ? 2 ft) and within 300 mm (12 in.) of every outlet box,
junction box, cabinet, or fitting. Flat cables shall not be
stapled on edge.
Sections of cable protected from physical damage by race-
way shall not be required to be secured within the raceway.
I don't either unless he wants to completely ignore the actual wording of the requirement.![]()
It is a strap ....
I have learned on the forums that some areas use cut of scraps of NM to support multiple runs of NM.
Wrapping one NM cable around two others before all three go into the box is a strap?