- Location
- New Jersey
- Occupation
- Journeyman Electrician
The wording of the "securing and supporting" rule would appear to prohibit one from running through studs horizontally since no staple or strap or similar device is used. But, I don't know of anyone that claims running an NM cable horizontally through studs requires any special securing or supporting regardless of the run length.
334.30(A) tells us that the cable within a bored hole is considered supported and secured.
334.30(A) Horizontal Runs Through Holes and Notches. In
other than vertical runs, cables installed in accordance with
300.4 shall be considered to be supported and secured
where such support does not exceed 1.4-m (4 1 ? 2 -ft) intervals
and the nonmetallic-sheathed cable is securely fastened in
place by an approved means within 300 mm (12 in.) of
each box, cabinet, conduit body, or other nonmetallic-
sheathed cable termination.