- Chapel Hill, NC
- Retired Electrical Contractor
680.12 states each means-- meaning each disconnect means-- which means --- possibly more than one. So for a pool, IMO you do not need a main breaker unless the panel is mounted remotely from the dwelling. This would bring 225.33 into play. If the MLO panel was used then the max of 6 handles could be used. In the 2014 code 225.36 has been changed which makes 225.33 okay for the 6 handle rule even if the panel is not suitable as service equipment-- in a new install
680.12 Maintenance Disconnecting Means. One or more
means to simultaneously disconnect all ungrounded conductors
shall be provided for all utilization equipment other
than lighting. Each means shall be readily accessible and
within sight from its equipment and shall be located at least
1.5 m (5 ft) horizontally from the inside walls of a pool,
spa, fountain, or hot tub unless separated from the open
water by a permanently installed barrier that provides a
1.5 m (5 ft) reach path or greater. This horizontal distance is
to be measured from the water?s edge along the shortest
path required to reach the disconnect.