mshields
- Boston, MA
A contractor has asked me if he can use 3 - 750 per phase for a 1600A service in order to take advantage of existing conduit he'd like to reuse.
At first glace I see that 3 - 750's at 475A each doesn't get you to 1600A under the 75 deg column of Table 310.15(B)16. I note that it would work if the conductors were rated for 90 degrees as 750's in that column are good for 535A (which times 3 is 1605A)
Under what conditions may I use the 90 deg column. I assume the conductor itself and the terminations would need to be rated for 90 degrees. Is it as simple as that?
Thanks,
Mike
Thanks,
Mike