luckylerado
- Lake of the Ozarks
Exception: Cables with entirely nonmetallic sheaths shall
be permitted to enter the top of a surface-mounted enclosure
through one or more nonflexible raceways not less
than 450 mm (18 in.) and not more than 3.0 m (10 ft) in
length, provided all of the following conditions are met:
(a) Each cable is fastened within 300 mm (12 in.),
measured along the sheath, of the outer end of the raceway.
(b) The raceway extends directly above the enclosure
and does not penetrate a structural ceiling.
(c) A fitting is provided on each end of the raceway to
protect the cable(s) from abrasion and the fittings remain
accessible after installation.
(d) The raceway is sealed or plugged at the outer end
using approved means so as to prevent access to the enclosure
through the raceway.
(e) The cable sheath is continuous through the raceway
and extends into the enclosure beyond the fitting not
less than 6 mm (1⁄4 in.).
(f) The raceway is fastened at its outer end and at
other points in accordance with the applicable article.
(g) Where installed as conduit or tubing, the allowable
cable fill does not exceed that permitted for complete conduit
or tubing systems by Table 1 of Chapter 9 of this Code
and all applicable notes thereto.
I have a fix for the KO plugs.
Talked to they guy I am helping. He said they drop romex into panels this way all over the county with no issues from AHJ.
I do not have any skin in this one. I am just a helper bee. I do not feel it will be unsafe to Mrs. Homeowner so I will not tell him I cannot lace the panel for him. I will grab a couple connectors on my way over there. Just trying to give him a shot in the arm to make the drywall deadline.
Thanks
All I see are mounting holes and those do not require closing.![]()
Look at the top of the panel where the 2" is KOed; There are a few 1/2" KOs that were knocked out when they KOed for the 2".:slaphead:
Why would you ask for advice if you knew how you were going to do it in the first place?
That being said, I would at least put a bell end on the ends of the PVC, and fill the openings with foam after all of the NM cables are in place.
If it was me I would use T & B #3201 for 1/2 KO or T & B #3202 for 3/4 KO
In this world of litigation, those burgers may end up not being free.
Just say a few years down the road there is a fire... a knowledgeable fire investigator becomes involved via an insurancd company wanting to find a reason not to cover the costs.
Humm Code violation... "Well, we had a master electrician install that"........
No good deed goes unpunishedand there is no such thing as a free burger
It's perfectly acceptable to sleeve Romex in 2" PVC.
A bushing is not required as it's PVC, not metal,
2011 NEC said:352.46 Bushings. Where a conduit enters a box, fitting, or
other enclosure, a bushing or adapter shall be provided to
protect the wire from abrasion unless the box, fitting, or
enclosure design provides equivalent protection.
2011 NEC said:(c) A fitting is provided on each end of the raceway to
but you do need to fasten all the cables within 12" of the pipe opening
2011 NEC said:(a) Each cable is fastened within 300 mm (12 in.),
the pipe should be under 2' long to maintain nipple status (for wire fill requirements).
2011 NEC said:through one or more nonflexible raceways not less
length
Also, you should put duct seal in the pipe opening when you're finished to prevent foreign materials from entering the panel (namely metal foreign materials).
2011 NEC said:(d) The raceway is sealed or plugged at the outer end
Some ECs stuff fiberglass insulation but this has been outlawed in my jurisdiction.
One thing I should mention though that since this panel is recessed, not surface mounted, sleeving is completely unnecessary,
.2011 NEC said:Cables with entirely nonmetallic sheaths shall
but it does make pulling a future circuit from an accessible location easier.
To start, let me make clear I know in many areas they allow the things I point out are NEC violations. That does not change the fact they are still NEC violtions
It depends on how you do it.
As pictured in the opening post it is without a doubt an NEC violation.
That is false
This first section is about PVC entering enclosures
This next section is specific to sleeving NM at a panelboard.
Part of 312.5(C) exception
You can't just have a raw end of PVC where the NMs go into it.
I agree.
That is a choice, not a requirement, the NEC allows 18" to 10'.
I agree
Outlawed? Perhaps just not approved.
The fact that this panel is recessed is one of the reasons it is an NEC violation
The NEC requires the end of these sleeves to be accessible.