Conduit size
nizak
9 #12 thhn cc conductors are installed in 3/4" emt and protected with 20A breakers. If the emt was 1.5" for example would that still be the max amount of conductors that could be installed for that scenario? Thanks
Correct, or even 4", Derating is not affected by conduit size.
Nine #12 CCCs on a 20A OCPD in any size pipe would be in violation of NEC. #12 Cu has ampacity of 25A [NEC310.15(B)(16)]. 310.15(B)(2)(a) calls for 70% derating for 7 through 9 CCCs, which leaves you with 17.5 amps.
EDIT: This is assuming you are using the 75 degree column.
In the late 20th century era on into the early 21st the magic number is Nine CCCs for fifteen or twenty amp circuits. Works out for single phase and three phase. I don't know if that was planned or serendipitous.
Oh, I wasn't familiar with the magic number table in the NEC :lol:
Not old enough to be a Beatles fan I guess.
The magic number works, although 210.4(B) is making it harder to get as many circuits in a 1/2" pipe as we used to and moving up to 3/4 doesn't help much. Who wants to bend 1" all day? I don't. Let's go buy some rolls of MC. While we're at it let's go get some guys that don't need to know anything about electrical to drag it around.
But why would you use the 75 degree column?
For the purposes of derating, unless we are using some odd wire, we can use the 90 degree column.
That means 9 CCCs 12 AWGs in a conduit can still use 20 amp OCP.
See 110.14(C) as to where you start your ampacity adjustment from.
Roger
Roger
110.14 is for terminations though, the conductors are still able to be adjusted from their 90 deg values (unless they are indeed 75 deg conductors). Final size of conductor selected however can not be smaller then whatever size the 60 or 75 degree terminals call for.
And where do you find this allowance?
Roger
Are we on the same page? I expect someone like you already knows this but maybe we are not talking about the same thing here causing some confusion.
It is not exactly stated in one simple sentence in one code section.
310.15 applies to the conductors - we make adjustments from 90 degree values if we have 90 degree insulation.
However after making adjustments we still must have a conductor no smaller then what is called for in the 60 or 75 degree columns of ampacity table for the sake of termination temperatures. That gets us back to what was mentioned about 110.14 Two different ampacities are required for same conductor in different portions of the conductor - the higher ampacity is what must be used, but don't know of any possible adjustments to termination ampacity, just to conductor ampacity only as it applies to it's insulation.
You can have a situation where ampacity adjustment says you can have a 6 AWG conductor for the temp rating of the insulation, but same application may need 4 AWG for the termination temperature - so in that case you still must use the 4 AWG.
Yes it is, read 110.14(C)
Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
Which is what 110.14(C) is saying
Yes it does.
I was just wondering what the point was to post #15
Roger
Yes it does.
Roger
Ok, 110.14 doesn't tell you how to make ampacity adjustments just that you can make them to the conductor. There is no adjusting the terminal, you will always have a conductor with a minimum size no smaller then the termination calls for, you can adjust the conductor ampacity as it applies to it's insulation, so you are starting (which that word start is what triggered my first reply) with the 90 degree column in the ampacity table as it relates to insulation not to the terminal that is likely only 60 or 75 degrees.
sorry for any confusion.