We started at the first light pole where the lighting circuit starts. It was difficult to see without the use of a bucket truck but what actually happened was the neutral was completely severed.
Whomever wired to this light pole originally tied the ground and neutral together and landed them on the floating neutral bar. The unfortunate part was that they used the bonding screw and bonded the floating neutral bar to the enclosure. I also mentioned that they used triplex instead of quad-plex from the original point of attachment to the volleyball area light polet………………..he breaker panel on that pole. Long story - short, all splices were re-made, the neutral bar is now floating and the problem was corrected. I left the 2 ground rods in place but removed the bonding to the fence. Thank you all for your advice and I'm truly sorry I didn't follow it from the start.
This sounds like one structures distribution was feeding a second structure. Keep in mind when you ran a feeder in the past from one structure to a second structure an equipment ground was not required to be run with the feeder in past era’s .
Second bonding of the neutral to the structures grounding electrode systems was required.
I would speculate the THHN that you discovered was green and was most likely some one trying to extend an equipment ground to some piece of equipment.
Seems to me what happened is you lost a neutral from one structure to another. I think we need to back up a little and pause before a determination is made that this was non- code compliant when installed
A separate equipment ground to a secondary structure is the norm today.
Am not sure if the feeder between the two structures originated in the primary building service distribution or a sub feed panel off of the primary buildings service distribution
One last comment if you read federal standard s on outdoor parks and outdoor recreational facilities you will discover that all metal fencing must be bonded to a ground rod and each fence opening must be bonded across that opening .
Edit: if your not receiving any type of federal funding you might not fall under federal quidlines