I was called to inspect and/or correct a shock hazard problem for outdoor lighting at the lake community facility where I live. There is a 4-circuit outdoor breaker panel mounted on a utility pole adjacent to a volleyball court. [*]The facility is fed by a 120/208V, 3 phase power to the club house
[*]The initial lighting circuit covering the basketball courts on the opposite side of the play area was 208 volts
[*]Wiring to that light circuit was run with triplex (seemed OK since no neutral was required at the time that was installed))
[*]Somewhere along the line (I guess when they created the volleyball area) someone decided to install 120 volt lighting and tapped off the 208 volt power line to the basketball courts. Now we're using the ground wire as a neutral I ran a temporary ground wire from the breaker panel to the fence post and that seemed to correct the shock hazard problem for now The power to the initial lighting scheme is 208V/1-phase. They didn't bring 3-phase out to the poles. I drove the 2 ground rods and bonded them to both the fence posts and the breaker enclosure. The lighting at this facility was installed in two separate phases and all were aerial runs. In addition there was a 120/240 volt service, telephone and CATV installed to the original clubhouse. remodeled about 15 years ago those original services, while disconnected in the street were never disconnected on the property or from the clubhouse and those original services, a tree fell in the basketball area and pulled the abandoned 120/240 volt triplex off the club house and utility pole along with the EGC portion of the service to the lights and the abandoned telephone and CATV wiring. Wiring to the basketball area is a 120/208v single phase circuit and was run with quad-plex. I climbed up on the roof to the clubhouse and noticed that the EGC for that circuit was disconnected so I bugged that together. Looking up to the light pole in the basketball area I can now see that the EGC is disconnected from that as well The neutral and both phases remained in tact. Someone (in their infinite wisdom) decided to extend the light circuit from the basketball area to the volleyball area by using tri-plex They used the EGC or strain relief wire as a neutral. When they came to play volleyball, barefoot in the sand a few players touched the fence and got a buzz. Just thought I'd post an update on this project.