david
- Pennsylvania
“Just thought I'd post an update on this project. We corrected the problem on wednesday.”
“Long story - short, all splices were re-made, the neutral bar is now floating and the problem was corrected. I left the 2 ground rods in place but removed the bonding to the fence.”
“we changed it this week to current standards.”
“It does have OC protection at the source. Both insulated conductors of the triplex are hot and the EGC (messinger cable) to the second light pole was spliced to the neutral at the first light pole. I had to use that as the neutral at the light pole where 120/240 is being utilized. It was run down the pole in PVC and was too short to get extended to the EG bar that I installed in the breaker panel. So, I inserted a piece of NM seal-tight over the bare messinger up through the threaded hub so it wouldn't ground to the metal enclosure and used the #12 THHN that was wrapped around the triplex as the EGC. I know it seems like a Rube Goldberg but that's what I had t work with.”
Are you sure that you changed this installations to current standards (code).