mwm1752
- Aspen, Colo
Is all of the area to the right of door wall space?
well if you start at the bottom point of the stairs you would have you first receptacle @ 6' max giving you a head room of approx 50-40" seems a bit silly for a general convienent use device.
Seems pretty cut and dried. All 14' is wall space under 210.52(A)(2), the definition of wall space has no minimum height or headroom requirement. So at least two receptacles are required to meet the 6' requirement of 210.52(A)(1).
Is there an argument to the contrary?
Cheers, Wayne
Like, "No one around here does it that way."Because this is a bunch of electricians there is definitely an argument to the contrary. None would be valid though. You nailed it.
I think what the OP presented was a more general question that assumed 6-12 spacing would be required in the application, but if it were a foyer then the 6-12 rule would not apply and you may not even need any receptacle on that particular wall in some cases like if it were also part of a hallway.Would that wall be part of a foyer? If so, one receptacle regardless of wall length
There is very limited required receptacles in non dwelling spaces.What if this was a commercial location?
I agree with Bob, current wording doesn't exclude anything here, that don't mean some inspectors won't overlook/ignore the low clearance and let you get by with less in that situation, or even deem a part of that space as not usable for whatever reason.
They get to deem it unusable more so then you do though.
Clearly you need a receptacle at the far right of the slanting wall so that you can easily plug in Christmas lights would around the stair railing.
Any other location would require an extension cord.
Could this be a situation where you should be thinking in terms of "better to have and not need, than need and not have"? And therefore place a receptacle where there is only 50" of headroom? Or at least, a junction box ready to receive a receptacle if it is required / if desired in the future?
Or is there a code rule that would prevent you from placing a receptacle in a location such as this?
I can see the low headroom location as a place where a resident might want to add a small lamp on a table, used for nothing other than the lamp.