240V Air Con vs 120V house

Status
Not open for further replies.

David.Solar

Member
Location
Los Angeles
Hi guys, I am new to this forum.

My grandma's house is an old house that runs 120V.
Recently she had an AC installer come out to install two AC units.
The AC units run on 240V. Doh!
How do I get the AC units to work? I've got varying responses from different people.

The AC Installer said: the line coming from the the utility line is 120V, get LADWP to come out to change the line to 240V and we should be good.
DWP rep said: need to upgrade the service panel + change the line
Friend who's not an electrician said: just need to upgrade the outlets that the AC units plug into to 240V

I don't know what to believe...

Pls help!

Thanks for reading and I hope I can help out in the future with any Solar PV questions as I am in the Solar industry.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You need to get a service change. You must call an electrician as you probably don't have the ampacity needed either
 

drspec

Member
Location
North Carolina
if what you are saying is true, then the HVAC company that sold them the equipment is scum.

they should have made sure the existing service was large enough and compatible with the equipment they are selling.
 

iwire

Moderator
Staff member
Location
Massachusetts
if what you are saying is true, then the HVAC company that sold them the equipment is scum.

they should have made sure the existing service was large enough and compatible with the equipment they are selling.

I think that is a bit harsh.

If the unit is 15 - 30 amps I don't think they would be expected to check the service size.

And as far as the service being 120 .... come on, you know that is ancient and should have been upgraded long ago.
 

drspec

Member
Location
North Carolina
I think that is a bit harsh.

If the unit is 15 - 30 amps I don't think they would be expected to check the service size.

And as far as the service being 120 .... come on, you know that is ancient and should have been upgraded long ago.


why is that harsh? every professional hvac company I have ever worked with always made sure the service was sufficient before selling a homeowner equipment.

The homeowner should have known that they would need a service change and upgrade before buying the equipment and imo the hvac company should have been professional enough to inform them of that.
 

kwired

Electron manager
Location
NE Nebraska
why is that harsh? every professional hvac company I have ever worked with always made sure the service was sufficient before selling a homeowner equipment.

The homeowner should have known that they would need a service change and upgrade before buying the equipment and imo the hvac company should have been professional enough to inform them of that.

Why do you think HVAC guys are going to know if the service can handle this?

Some are better with electrical knowledge than others, but at same time it sounds like these are smaller units that probably will not need major electrical upgrades in 95%+ cases. HVAC guy maybe never even realized there is no 240 volts available.

Existing 120 service possibly doesn't have the capacity needed even if you had the same sized units in 120 volt versions.
 

drspec

Member
Location
North Carolina
Why do you think HVAC guys are going to know if the service can handle this?

Some are better with electrical knowledge than others, but at same time it sounds like these are smaller units that probably will not need major electrical upgrades in 95%+ cases. HVAC guy maybe never even realized there is no 240 volts available.

Existing 120 service possibly doesn't have the capacity needed even if you had the same sized units in 120 volt versions.

if they were plug in window units, why would they assume there were receptacles close enough to plug into?

if they were central air units where none previously existed, why would they assume anything?
 

kwired

Electron manager
Location
NE Nebraska
if they were plug in window units, why would they assume there were receptacles close enough to plug into?

if they were central air units where none previously existed, why would they assume anything?

I didn't mean that no branch circuits wouldn't possibly need to be run. But adding a couple 15 amp or less window A/C units usually doesn't require additional service capacity.
 

drspec

Member
Location
North Carolina
I didn't mean that no branch circuits wouldn't possibly need to be run. But adding a couple 15 amp or less window A/C units usually doesn't require additional service capacity.


and don't you think they should have let the homeowner know that an electrician would probably need to get involved?

that way they could have known if the purchase of the ac units along with the needed electrical work was within their budget
 

kwired

Electron manager
Location
NE Nebraska
and don't you think they should have let the homeowner know that an electrician would probably need to get involved?

that way they could have known if the purchase of the ac units along with the needed electrical work was within their budget
That would be nice, but I don't expect it to happen either, I have encountered much worse incidents of someone like HVAC guys installing something and then owner finds out they need to make some fairly significant changes to be able to power it.

How about something like what happened in this thread?
 

PetrosA

Senior Member
Maybe this is regional, but here in SE PA I wouldn't ever expect to find a 120V service still in use in a house. I guess it could happen, but I haven't seen one since the 1980s. For it to happen the service would have to be over 50 years old at least and I would only even suspect it if I saw fuses in the house rather than breakers. But again, haven't seen them in a long, long time...
 

kwired

Electron manager
Location
NE Nebraska
Maybe this is regional, but here in SE PA I wouldn't ever expect to find a 120V service still in use in a house. I guess it could happen, but I haven't seen one since the 1980s. For it to happen the service would have to be over 50 years old at least and I would only even suspect it if I saw fuses in the house rather than breakers. But again, haven't seen them in a long, long time...
I think what you described is almost exactly what you will find if you run into a house with a 120 volt only service almost anywhere.
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
While it may be true that the house is only fed with 120v there may still be 240 availible. What I ususally see is that a triplex is run but one of the wires is capped off. The reason is that usually the utility wire will go bad before the service does.

Now that's not to take away from the fact that your old A-base meter will still need to be changed.

And while I agree that the AC guys might have seen a 100 amp service and thought nothing of it and, of course, just assumed that there was 240V availible. I still think that the owners should have some recourse. This is about a $4000 mistake, give or take. If it was made at my house I would have to worthless AC units sitting there.
 