erock1
- Houston, Tx
So the debate is, is a line to neutral a current carrying conductor. The paragraphs in sec. 310.15 5 a and b are a little unclear. Could some one clear this up for me.
In typical US wiring, there are only three general scenarios where the neutral DOES NOT count as a current carrying conductor:I guess what I'm trying to figure out is for just a single circuit, like you stated if they is 20 amp on a phase and 0 on b phase the neutral has 20 amp of current. That being said then 1 hot and 1 neutral will always have the same current on it, meaning that I would have to derate the neutral on a single circuit.
The way he wrote that makes it hard to determine exactly what he means. If you go by the context of the first sentence for the second... he still has a 3-wire circuit, and the neutral would not count even though it has 20A of current on it...because the b phase conductor has zero, and it does count. The reason for the neutral not counting is that you never have more than an arithmetic sum of 40A current on all three wires.I think you mean that you would count the neutral as a current carrying conductor. Yes you would.
Physics, not code.
For 1Ph Line = Neutral
For 3Ph In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))
Neutral Conductors:
Here's some examples of when to count and not count the neutral as a current
carrying conductor or CCC:
3Ø- 208Y/120 or 480Y/277 volt system-different circuit types:
A) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
B) 3 wire circuit w/ 2 ungrounded, 1 neutral = 3 CCC's
C) 4 wire circuit w/ 3 ungrounded, 1 neutral = 3 CCC's*
Notes:
A) A normal 2 wire circuit has equal current flowing in each of the circuit
conductors so they both count as CCC's.
B) In this circuit the neutral current will be nearly equal to the current in the
ungrounded conductors so the neutral counts as a CCC
C) In this circuit the neutral will only carry the imbalance of the current between
the three ungrounded conductors so it is not counted as a CCC, with an exception,
*if the current is more than 50% nonlinear (see below for NEC article 100
definition) then the neutral would count as a CCC.
1Ø- 120/240 volt system-different circuit types:
D) 2 wire circuit w/ 1 ungrounded, 1 neutral = 2 CCC's
E) 3 wire circuit w/ 2 ungrounded, 1 neutral = 2 CCC's
Notes:
D) A normal 2 wire circuit has equal current flowing in each of the circuit
E) In this circuit the neutral will only carry the imbalance between the two
ungrounded conductors so the neutral is not counted as a CCC.
Nonlinear Load. A load where the wave shape of the steady-state current does
not follow the wave shape of the applied voltage.
Informational Note: Electronic equipment, electronic/electric-discharge lighting,
adjustable-speed drive systems, and similar equipment may be nonlinear loads.
©Rob Meier 2014
That is not true for a 1Ø 3-wire circuit....For 1Ph Line = Neutral...