Lady Engineer
- New Jersey
I have an existing plant where we have a 800A, 480V, 4 wire system. The system is fed from a 3ph, 4W 500KVA pad mount. We also have a generator rated 4 Wire. The reason for it is because the generator and main are GFP breakers, and ATS is 4 pole (contactor type). The generator is a separately derived system, at least I hope it's grounded or bonded, correctly.
The client's engineer is saying that we don't need the neutral because we can only connect 3 phase loads to the main switchboard and used step downs for single phase, single pole loads, which I agree. I'm replacing the four pole ATS with a 3 pole, eliminating the GFP, replacing the switchboard, replacing the grounding on both the service and generator.
Question: Since the generator is also 3ph, 4W, do you see an issue? I'm trying to trouble shoot, even though I can't think of anything. He's insisting on a 3W service, and I'm not one argue. It's hard dealing with EEs with a PE. Hahaha...(yes, I'm one!)