But you have to provide a supply side bonding jumper which will be the same size.Where I don't need the neutral for L-N loads immediately, I like to bond the N-G at the first legal opportunity, then not bring the neutral downstream to ATS's. It avoids the cost of the neutral, but it also avoids the age old argument for a 4 pole ATS, which is should the neutral be open transition, or overlapping (closed) transition switching.