I'm trying to identify / locate what appears to be a partial(?) ground fault on a rather unusual piece of industrial equipment. It's a 2MVA 3 phase transformer with a 4160 primary and an infinitely variable ( between 35 and 250 volt) secondary. The primary is connected in delta. The secondaries are brought out of the can as 6 terminals. The best way to describe the secondary is it's construction could be thought of as a multi turn power rheostat. The secondary is connected in delta (floating)
The purpose of these strange units is to melt glass by energizing electrodes that are submerged in the molten glass pool. Yeah, I thought glass was an insulator, but when it's heated to a "glowing" temperature it conducts very well.
Each phase conductor that supplies the electrodes consists of 12 530mcm locomotive cables. The normal running amperage to each electrode is just under 6,000 amps. The normal voltage phase to phase is around 180 volts.
We have two of these units and one displays voltage to ground measurements like what you would expect from a floating delta system. The problem child has the "vector center" skewed by approximately 15 volts. The measurements recorded yesterday while under load were:
1. A phase 110 volts to ground.
2. B phase 89 volts to ground.
3. C phase 125 volts to ground.
The 89 volts leads me to believe that the phase is not "solidly" faulted to ground.
I have "some experience" troubleshooting "floating ground" and "high resistance ground" systems. I tried a few of my tricks and they failed or confused me.
Extensive resistance and meggar tests have been performed when the equipment was not in production, no "smoking guns" were found.
I tried using a "wiggy" (.1 amp) as a small load to swing the "vector center" from center when the system was under load, this produced no visible change.
I tried using a 500 watt quartz light (4 amp nominal load) to swing the vector center, this produced:
1. When applying the quartz light to ground and A phase, it lowered the voltage 4 volts.
2. When applying the quartz light to ground and B phase, it lowered the voltage 2 volts.
3. When applying the quartz light to ground and C phase, it lowered the voltage 4 volts.
I was able to lift the electrodes out of the melt pool and energize them (at the minimum voltage). My results were:
1. A phase 24 volts to ground.
2. B phase 20 volts to ground.
3. C phase 22 volts to ground.
As you can see the B phase still read the lowest, but what I found interesting is that A & C swapped in intensity, voltage to ground.
My opportunities for testing are severely limited by production. What I would like to get from the community is a list of their tricks or suggestions on what to test.
The purpose of these strange units is to melt glass by energizing electrodes that are submerged in the molten glass pool. Yeah, I thought glass was an insulator, but when it's heated to a "glowing" temperature it conducts very well.
Each phase conductor that supplies the electrodes consists of 12 530mcm locomotive cables. The normal running amperage to each electrode is just under 6,000 amps. The normal voltage phase to phase is around 180 volts.
We have two of these units and one displays voltage to ground measurements like what you would expect from a floating delta system. The problem child has the "vector center" skewed by approximately 15 volts. The measurements recorded yesterday while under load were:
1. A phase 110 volts to ground.
2. B phase 89 volts to ground.
3. C phase 125 volts to ground.
The 89 volts leads me to believe that the phase is not "solidly" faulted to ground.
I have "some experience" troubleshooting "floating ground" and "high resistance ground" systems. I tried a few of my tricks and they failed or confused me.
Extensive resistance and meggar tests have been performed when the equipment was not in production, no "smoking guns" were found.
I tried using a "wiggy" (.1 amp) as a small load to swing the "vector center" from center when the system was under load, this produced no visible change.
I tried using a 500 watt quartz light (4 amp nominal load) to swing the vector center, this produced:
1. When applying the quartz light to ground and A phase, it lowered the voltage 4 volts.
2. When applying the quartz light to ground and B phase, it lowered the voltage 2 volts.
3. When applying the quartz light to ground and C phase, it lowered the voltage 4 volts.
I was able to lift the electrodes out of the melt pool and energize them (at the minimum voltage). My results were:
1. A phase 24 volts to ground.
2. B phase 20 volts to ground.
3. C phase 22 volts to ground.
As you can see the B phase still read the lowest, but what I found interesting is that A & C swapped in intensity, voltage to ground.
My opportunities for testing are severely limited by production. What I would like to get from the community is a list of their tricks or suggestions on what to test.