YepperI think the reason for the ungrounded delta secondary is the classic one.
Losing the heat source unexpectedly with the furnace full of glass could be catastrophic for the equipment.
With an ungrounded circuit a single fault to ground anywhere will not disable the heater, allowing time to do a controlled shutdown (even finishing the batch normally) and then make the necessary repair.
Does the other glass melter have one or more ground straps?
How does the glass initially get hot enough to conduct to use resistive heating via current thru the glass?
.
.
I think the reason for the ungrounded delta secondary is the classic one.
Losing the heat source unexpectedly with the furnace full of glass could be catastrophic for the equipment.
With an ungrounded circuit a single fault to ground anywhere will not disable the heater, allowing time to do a controlled shutdown (even finishing the batch normally) and then make the necessary repair.
160131-2114 EST
Ingenieur:
If there is no path to earth other than the ground strap, then there is no current flow. Within the variable transformer there may be some resistive leakage, but possibly more capacitive leakage. Under normal conditions these would be very small compared to 6000 A.
When milldrone connected his 500 W bulb, then there was a flow of about 4 A. This is small compared to 6000 A, but measurable, and it provided a method to estimate the leakage path source impedance (electrodes to glass, to brick or thru brick, to metal kettle, to grounding strap, and thru earth.).
Possibly this is an indication of a failure in the kettle lining.
.
160131-1635 EST
milldrone:
Put an AC current meter around the ground strap. By your use of the singular I assume there is only one ground strap. Initially you may or may not see much cutrrent at all, hopefully near zero. Apply your tungsten lamp load from one phase to earth. The ground strap current should change by about the amount of current thru the lamp load. If without the lamp load the current is zero, then with the lamp load the lamp current should equal the ground strap current.
.
160131-2114 EST
Ingenieur:
If there is no path to earth other than the ground strap, then there is no current flow. Within the variable transformer there may be some resistive leakage, but possibly more capacitive leakage. Under normal conditions these would be very small compared to 6000 A.
When milldrone connected his 500 W bulb, then there was a flow of about 4 A. This is small compared to 6000 A, but measurable, and it provided a method to estimate the leakage path source impedance (electrodes to glass, to brick or thru brick, to metal kettle, to grounding strap, and thru earth.).
Possibly this is an indication of a failure in the kettle lining.
.
...
phase to phase volts A-B 171.3, B-C 171.8, C-A 172.8
volts line to ground A 104.3, B 76.4, C 113.3
Amperes A 5100, B 5426, C 5282
Can you calculate where between the two lower voltage electrodes the hypothetical fault in the vessel insulation might be from those vectors?the glass Z (load) is not balanced
Ph V/(i/sqrt 3)
0.058
0.024
0.057
not a balanced load
shifts center point
The load on the 'good' transformer is balanced
0.035
0.032
0.033
almost perfect
I previously calculated the phasors based on the phase shift being consisrent on all 3 phases
when I back calculated the ph-ph V the phase angles were maintained within a few degrees when normalized for the 30 deg ph to N shift