Paul the BIG Finn
- Ashburn, VA
The owner has selected a 3+1 wiring package for the systems furniture. The systems furniture has an internal wiring harness with 3 circuits sharing a neutral and ground wire PLUS a separate power circuit with a dedicated neutral and dedicated ground for that circuit. The concept is for the dedicated circuit to be powered from a UPS and serve critical loads with the other three circuits supplied from a standard panelboard to serve the non critical loads.
The electrician is balking at installing the system citing NEC 210.4's requirement that "All conductors of a multiwire branch circuit shall originate from the same panelboard or similiar distribution equipment." NEC 210.4(B) further requires all multiwire branch wiring must be disconnected from a single point.
As I interpret the code we have one multiwire branch circuit and a single separate circuit powering the workstations. The electrician says that since they are connected to the same "whip" which then plus into the workstation it is a single multiwire circuit and all of the circuits must be disconnected together and be supplied from the same panelboard.
What is the board's opinion?