From table 8, the resistance for coated copper # 14 at 75c is 3.39 ohms per k/ft, is this ok to use for 14/2 NM? If so how, far can you run this cable?
Last edited:
From table 8, the resistance for coated copper # 14 at 75c is 3.39 ohms per k/ft, is this ok to use for 14/2 NM? If so how, far can you run this cable?
How many load amps will it be carrying? Or do you want to assume that it will be the max allowed current?
Do you have specific voltage drop sensitivity or would you just want to follow the 2%, 3% informal guidelines?
Thanks for the calculator. In a residential application how would I figure the load and the number of outlets , lights, that would be allowed by code if I did not know the actual load?Southwire online calculator says 56 feet.
Southwire online calculator says 56 feet.[/QUOTE
Thanks for the calculator. In a residential application how would I figure the load and the number of outlets , lights, that would be allowed by code if I did not know the actual load?
Is it based on 3va per sq ft. Calc. Still won't give the number of outlets .It will however,give me the number of circuits. How many outlets? As they add resistance???
Or should I just stick to 80% of 15amp = 12 amps and stay with 56 feet to provide max load capacity to serve the possibility of having a full load of 12amp then I know i'm good??
Also would I use 3.19 ohms per k/ft from table 8 when calculating my esistance ????
Can anyone answer the above?
Sparks, please do not continue to start new threads on this topic, you can post questions in this thread.
Roger
In a residential application the number of circuits is based on the 3va, not the number of outlets, and I don't believe the conductors in NM are coated.
The neutral and phase conductors are coated (insulated) with the ground being bare (NM-B). A general rule of thumb is ten openings per home run. Like 4 receptacles and 1 light x 2 rooms. If you know you have a specific need though, that's another issue.
Is coated insulated? I was under the impression it was tinned but can't find the reference in the code. Hopefully someone will post that.
Concerning the number of outlets, the load should be considered as the OP stated, but no limit on outlets being residential.
So tinned = coated? what is tinned?
You can put as many receptacles as you want on a 15A or 20A circuit. More receptacles does not mean there will be more load on a circuit. This is one area where the code has not crept in and become a design manual.Thanks for the calculator. In a residential application how would I figure the load and the number of outlets , lights, that would be allowed by code if I did not know the actual load?
Is it based on 3va per sq ft. Calc. Still won't give the number of outlets .It will however,give me the number of circuits. How many outlets? As they add resistance???
Or should I just stick to 80% of 15amp = 12 amps and stay with 56 feet to provide max load capacity to serve the possibility of having a full load of 12amp then I know i'm good??
Also would I use 3.19 ohms per k/ft from table 8 when calculating my esistance ????
Magnet wire in motors and transformers has a thin, tight, polymer insulation on it and it conducts great.Coated to me always meant it had some type resin around it, like the coils in transformers.
EDIT electricity runs on the surface of wire right? So a chemical coating seems like it would impede the flow more than a plastic / rubber matter sitting on top of the surface.