Fire alarm splice

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If you have a device in a loop that's to be removed and splicing is not allowed what do you do? Pull back out the cables the run new cable from prev device skipping abandoned one to the next device? Thanks
 

iwire

Moderator
Staff member
Location
Massachusetts
Depends on the reason for removing it.

Does the box have to be removed as well or can I blank it up?

Depends on local rules, in MA a wire nut splice is fine, in RI it is prohibited.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
If you have a device in a loop that's to be removed and splicing is not allowed what do you do? Pull back out the cables the run new cable from prev device skipping abandoned one to the next device? Thanks

You could install a terminal block. That is an acceptable method in many jurisdictions. Space Age Electronics has a nice product here.

space age.jpg
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
:thumbsup:

Yes, that is what they want.

I just noticed that the OP is in my neck of the woods. The "no splice" requirement must be a spec or manufacturer's thing because NJ doesn't care.
 