MD84
- Stow, Ohio, USA
There is also the resistance of the ungrounded conductor. That is larger however.
Re: Gene B:
In any case, the greatest danger comes from the possibility of a compromised EGC, not the window of vulnerability between a ground fault occurring and the breaker tripping.
I see what you are saying and there is some truth to it. I do feel however that the duration of the fault contributes quite a bit to the overall hazard of the fault. Not only does the duration increase the probability of someone getting shocked it also increases the possibility of a lethal shock. The severity of a shock not only depends on the voltage exposure but also the duration current is flowing.
I do have some actual data to contribute.
480v Y
50A Seimens BQD 2 Pole CB (brown and orange phase)
130A measured at CB Load Side brown phase during fault
30A measured in first JB EGC during fault
150' 1 AWG Copper to first JB
300' 1 AWG Copper to first Pole
180' 8 AWG Copper to faulted Pole
3' 10 AWG Copper to fault location inside Pole
8 AWG Copper EGC returning the same route as above (630')
That is 0.172 ohms for the ungrounded conductor and 0.396 ohms for the EGC. A total of 0.568 ohms for the circuit. This does not include any resistance of splices or the impedance of the fault.
This is a relatively low resistance circuit and if the full circuit voltage was present there would likely be current in or approaching the instantaneous trip range.
Re: Gene B:
480v Y