jumper
- 3 Hr 2 Min from Winged Horses
By definition stranded wire is a flexible connection. Does the code not require flexible connections to be terminated with a terminal ( sta-kon) connection on a screw unless the screw is rated for this( i.e. a breaker terminal screw)
110.14(A)(A) Terminals.
Connection of conductors to terminal parts
shall ensure a thoroughly good connection without damag-
ing the conductors and shall be made by means of pressure
connectors (including set-screw type), solder lugs, or
splices to flexible leads. Connection by means of wire-
binding screws or studs and nuts that have upturned lugs or
the equivalent shall be permitted for 10 AWG or smaller
conductors.