What is a reasonable/acceptable voltage drop across a 200A 120/240V main breaker?
Also known as "fall of potential".
I read .23V on each leg from line to load.
Here is the reason for checking. I had a customer call saying their dryer quit working along with the bath lights. Then it would come back on, on it's own.
So I go to the customer and turned the dryer on and the bath lights. I noticed the light had a slight dimming/flicker. The dryer was still running. I checked the voltage and had around 244V L-L and 122V L-N. So I just left the dryer running and the light on.
After about 5 min. I heard the dryer quit and I looked in the bath and the lights were off. I rushed over to the panel and checked voltage. I read 240+ L-L but the "A" leg only had 70-80V L-N, "B" had 120V. I then went back to "A" leg and it was back up to 120V. The lights were back on but, of course, the dryer had to be restarted, which it did start back.
This all sounds like the classic case of losing a leg and some of the 120V things would come on when a 240V load was on because of back feeding through the bus.
Strange thing is only the bath lights would quit when the dryer stopped. I couldn't find any other load that wasn't working.
I checked all connections on everything in the panel, ie; breaker terminals, main lugs, neutral lug and bus.
I found a few loose but not bad. I stayed about 30 min. more and never could get it to lose voltage again. Long day so I headed home. I talked to the HO on the phone as she wasn't home and told her to call POCO to come and check their connections. I had checked voltage before the main at the lugs so I knew it was either in the meter or one of the POCO connections.
Now after I get home the lady calls me and says POCO came and checked it. The problem showed up while they were there. They told her to tell me to replace the main breaker. I asked if they checked it and she said no they weren't allowed to. I asked if they checked their splices and she said all they did was pull the meter and check the voltage. No load on it or anything.:roll:
Anyway, I don't think it is the main breaker because I saw the low voltage before the main.
Any thoughts?
Also known as "fall of potential".
I read .23V on each leg from line to load.
Here is the reason for checking. I had a customer call saying their dryer quit working along with the bath lights. Then it would come back on, on it's own.
So I go to the customer and turned the dryer on and the bath lights. I noticed the light had a slight dimming/flicker. The dryer was still running. I checked the voltage and had around 244V L-L and 122V L-N. So I just left the dryer running and the light on.
After about 5 min. I heard the dryer quit and I looked in the bath and the lights were off. I rushed over to the panel and checked voltage. I read 240+ L-L but the "A" leg only had 70-80V L-N, "B" had 120V. I then went back to "A" leg and it was back up to 120V. The lights were back on but, of course, the dryer had to be restarted, which it did start back.
This all sounds like the classic case of losing a leg and some of the 120V things would come on when a 240V load was on because of back feeding through the bus.
Strange thing is only the bath lights would quit when the dryer stopped. I couldn't find any other load that wasn't working.
I checked all connections on everything in the panel, ie; breaker terminals, main lugs, neutral lug and bus.
I found a few loose but not bad. I stayed about 30 min. more and never could get it to lose voltage again. Long day so I headed home. I talked to the HO on the phone as she wasn't home and told her to call POCO to come and check their connections. I had checked voltage before the main at the lugs so I knew it was either in the meter or one of the POCO connections.
Now after I get home the lady calls me and says POCO came and checked it. The problem showed up while they were there. They told her to tell me to replace the main breaker. I asked if they checked it and she said no they weren't allowed to. I asked if they checked their splices and she said all they did was pull the meter and check the voltage. No load on it or anything.:roll:
Anyway, I don't think it is the main breaker because I saw the low voltage before the main.
Any thoughts?