- Tennessee NEC:2017
- Semi-Retired Electrician
UPDATE
UPDATE
Well, I got another call late today saying the customer had lost power to a well pump along with the previous items. I asked if the POCO had been called back. She said yes but they wanted me there first or at the same time in case they needed to cut the power while I checked in the meter.
When I got there (no POCO yet) I checked the voltage at the panel and had nothing on the "A" leg, and that was ahead/before the main breaker. Which proved, a 2nd time, that it wasn't the main breaker.
I waited for the POCO and when they got there the lineman headed straight for the meter to pull it. Before he could even get the seal cut he saw the digital read out went to "0".
So he knew something was wrong on their end.
He went up to the transformer and found one leg had almost burnt in two. Said it looked like a squirrel or some "critter" had gotten in it.
I hated to charge the customer for another trip since I told her yesterday that the POCO should have checked everything when they were there. But it was a 50 mile round trip and after hours to boot.
I just don't understand why POCO won't check everything when they are there instead of having to be called back!:rant:
UPDATE