Buck Parrish
Senior Member
- Location
- NC & IN
I am installing two 225K and three 150K. 480 Delta to 120/208 Wye
There is no building steel to bond to. Water lines are plastic. Some one was telling me to install a ground rod at each one. To me that didn't seem correct.
I thought all I need at my primary is the three phases and the equipment ground. Then some body else is saying well pull a neutral and an equipment ground on the primary?.
Since each location is a newly derived electrical system. Must we isolate the grounds on the secondary disconnect / 200 amp 3 phase panel
Which is correct? Or maybe both ways are correct, or neither?
.
I've also been told I can adjust the 208 volts on my secondary. To a higher voltage. What are your thoughts on that?
Thanks for the help in understanding the inner windings of the transformers
Thanks
There is no building steel to bond to. Water lines are plastic. Some one was telling me to install a ground rod at each one. To me that didn't seem correct.
I thought all I need at my primary is the three phases and the equipment ground. Then some body else is saying well pull a neutral and an equipment ground on the primary?.
Since each location is a newly derived electrical system. Must we isolate the grounds on the secondary disconnect / 200 amp 3 phase panel
Which is correct? Or maybe both ways are correct, or neither?
.
I've also been told I can adjust the 208 volts on my secondary. To a higher voltage. What are your thoughts on that?
Thanks for the help in understanding the inner windings of the transformers
Thanks