Let's say you go to a common GEC busbar and amp clamp the conductors terminating there. You see 5, 7, 9, 12, 23, ... amps each conductor terminating there. Is it objectionable? Is it a violation? This would assume the wiring itself is compliant.
.
Nowhere enough info to say.
Could be fine, could be a problem, might even be hazardous.
But just because there is current on an EGC does not make it automatically objectionable current.
In some instances size of the signal may not matter, if it interferes with normal operation.
Again, the equipment is designed poorly if the 'noise' on EGC supplying it causes an issue.
Even if it does occur in some manner, there is a way to construct the GEC system in a way that would meet someone's opinion of best practice
This is they type of thinking that leads to voodoo grounding schemes such as triad ground rods etc.