Do you have to have a plastic bushing on a pvc pipe if romex or uf wire is going into a piece of pipe without a connector by code? This is 12-2 not big wire.
Is this just a sleeve? Just deburr the inside edge.
300.16 requires a bushing.
For a raceway containing conductors, I agree.
I was referring to a cable in a sleeve. No bushing required.
Sorry, wrong section.
300.15 (C) applies to cables leaving conduit where there is no box.
"A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion."
Ok, I agree and change my position. :ashamed1: A bushing is required.
(C) Protection.
A box or conduit body shall not be re-
quired where cables enter or exit from conduit or tubing
that is used to provide cable support or protection against
physical damage. A fitting shall be provided on the end(s)
of the conduit or tubing to protect the cable from abrasion
352.46 Bushings.
Where a conduit enters a box, fitting, or
other enclosure, a bushing or adapter shall be provided to
protect the wire from abrasion unless the box, fitting, or
enclosure design provides equivalent protection.
I am not so sure that a bushing is required for PVC in all cases, especially a cable through a sleeve.
300.15(C) says fitting not bushing.
And a sleeve is not included in 352.46
A bushing is a fitting. Look up the definition of 'fitting' in Article 100.
"Fitting: An accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a mechanical rather than an electrical function."
Article 300 applies to all of Chapter 3.
Yes a bushing is a fitting, but not all fittings are bushings. Why wouldn't a just a male adaptor be acceptable?
I have to take off for a while. You pose a good question. I don't have time to investigate, but I will later. I have to go meet my daughter's new puppy for the first time.
:thumbsup:
I am not so sure that a bushing is required for PVC in all cases, especially a cable through a sleeve.
300.15(C) says fitting not bushing.
IMO, the use of "fitting" opens one to using PVC male adapters, PVC bell ends, and, in the case of EMT, knock-on Arlington "conduit cap" like the EMT50C that is shoved onto the raw end of the EMT
Also allowed would be go-froms such as
Bring back pics of the puppy.
IMO, the use of "fitting" opens one to using PVC male adapters, PVC bell ends, and, in the case of EMT, knock-on Arlington "conduit cap" like the EMT50C that is shoved onto the raw end of the EMT
Also allowed would be go-froms such as
IMO, the use of "fitting" opens one to using PVC male adapters, PVC bell ends, and, in the case of EMT, knock-on Arlington "conduit cap" like the EMT50C that is shoved onto the raw end of the EMT
Also allowed would be go-froms such as