I would check the GFCI because most are rated 120v/240v not 208V. I believe they make them 208V
Sounds like hooking up the breaker isn't your biggest problem. Make room in the existing conduit or run a new one.I want to put the gfci in line with the 2 hots and a egc the conduit is full I cant pull more wire they want gfci 20 feet from pump the panel is 100 feet from where they want the gfci.
But if the manufacturer has not done the required UL tests in the 120/208 configuration they will not sanction it's use in that configuration and an AHJ is likely to reject it as contrary to listing.A two pole GFCI in a 120/240 volt or a 120/208 panel would work the same the gfci works on 120 volts of each leg.
Sounds like this is a customer requirement, not Code.Why do you want to install a GFCI on the pump?
There is a 32V differential in potential as well as 3ph being 120* between hots vs 180* for 120/240V. GFCI may not care about that but there have been threads here re: 120V AFCI breakers not working correctly/rated for 208V service.
That has nothing to do with how a gfci works.
Which I stated, not clearly enough. The main point that I (and GoldDigger in the post before) was getting at is that a 2p GFCI breaker may not be rated or listed for 208V. Some are, like this one:
"The Siemens 2-pole GFCI circuit breaker can be installed on a 120/240V AC single phase, 3 wire
system, the 120/240V AC portion of a 240/120 volt, 3 phase, 4 wire system, or on a 208Y/120 volt, 3 phase, 4 wire system. When installed on these systems, protection is provided for 2 wire, 240V AC or 208V AC circuits; 3 wire, 120/240V AC circuits."
Irrelevant here, but noteworthy, is that the 120V 1p breakers are not listed for 120/208V.
As for the rest of my post, it was on point to the question you asked:
"how can I wire the gfci with no neutral ?"
Standard 2 pole breakers are only listed 120/240 yet we use them on 208 quite often.