I have a Milbank meter/panel combo pedestal feeding a sub-panel.  (240/120v 1-ph 3w)
In the Milbank pedestal panel, there is a 60A 2pole breaker that feeds a separate sub-panel next to it.
The 60A 2P breaker is installed in a position where the two poles are fed from the same leg in the Milbank panel. (so, 120v to ground on each pole, but basically zero volts between them)
The multi-wire branch circuits in the subpanel have been nuisance tripping. They are 20A 2pole breakers, and share a neutral, to feed 120v circuits.
The sub-panel was obviously meant to be fed 240/120 and share neutrals, but in this case the two main lugs are fed from the same leg of the service.
I can see how this could possibly overload a neutral, but is there any reason they would trip the 20A breaker? I don't see that right off...
I can easily correct this by trading positions of a few of the breakers in the Milbank panel, but was just curious if it might cause a breaker to trip.
Thanks, sorry if this is a dumb question
    Jeff