What size breaker can I use for this pool pump motor ?

Status
Not open for further replies.

bluecollar84

Senior Member
Location
US
5ef25fc5e2b16b529395c13013d23ed4.jpg


Sent from my SM-G935V using Tapatalk
 

bluecollar84

Senior Member
Location
US
The pool propane heater is on the same circuit it draws like 1.5 amps does this change your answer ?

Sent from my SM-G935V using Tapatalk
 

bluecollar84

Senior Member
Location
US
Also what wire Guage do I need for 120 feet of branch circuit wiring from breaker to pump in underground conduit ?

Sent from my SM-G935V using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Also what wire Guage do I need for 120 feet of branch circuit wiring from breaker to pump in underground conduit ?

Sent from my SM-G935V using Tapatalk

to be compliant a #12 will do however you will have about a 6 volt drop-- probably fine but #10 wouldn't hurt
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You do realize that Hayward pumps are notoriously troublesome with Hayward pumps.... A dp 20 amp gfci should work
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You still cannot have the heater on a 30 amp circuit

210.23 Permissible Loads, Multiple-Outlet Branch Circuits.
In no case shall the load exceed the branch-circuit
ampere rating. A branch circuit supplying two or more outlets
or receptacles shall supply only the loads specified
according to its size as specified in 210.23(A) through (D)
and as summarized in 210.24 and Table 210.24.
(A) 15- and 20-Ampere Branch Circuits. A 15- or
20-ampere branch circuit shall be permitted to supply
lighting units or other utilization equipment, or a combination
of both, and shall comply with 210.23(A)(1) and (A)(2).

(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit
shall be permitted to supply fixed lighting units with
heavy-duty lampholders in other than a dwelling unit(s) or
utilization equipment in any occupancy. A rating of any one
cord-and-plug-connected utilization equipment shall not
exceed 80 percent of the branch-circuit ampere rating.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
How are the pump and propane heater NOT utilization equipment as per 210.23(B)? :?


So you are saying that a pump cannot be on a 30 amp breaker? If so look at 430.52---Motors are a different animal. Still not sure of what you are asking. I think the pump and heater are utilization equipment but pumps have an article unto themselves. The heater does not get permission in 210.23(B) as far as I can tell.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
So you are saying that a pump cannot be on a 30 amp breaker? If so look at 430.52---Motors are a different animal. Still not sure of what you are asking. I think the pump and heater are utilization equipment but pumps have an article unto themselves. The heater does not get permission in 210.23(B) as far as I can tell.

Okay, I'm totally confused. It looks like 210.23(B) permits more than one utilization equipment as long as none of them exceed 80% of the circuit rating (30 amps). Are you saying that the 250% allowed for in-rush (12 x 2.5 = 30) applies to this limit?
 
Sounds like this application is out of the normal for a pool propane heater and filter pump. I did some quick checking and found that it is an option to tap power from the time clock or the switch. The switch I presume would replace the recepticle and become the disconnect. Then hard wire from there. Don't know if this is an option for your application.


Sent from my iPhone using Tapatalk
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I wire these pumps all the time on a 20A circuit and even wire in the heater on the same circuit with no problems. They typically pull around 15A on 120V, 7 or 8 on 240V.
 