I wire these pumps all the time on a 20A circuit and even wire in the heater on the same circuit with no problems. They typically pull around 15A on 120V, 7 or 8 on 240V.
You run the propane heater and the pump cord and plug to a duplex receptical? This pump running is drawing only 10 amps. But I was to the understanding it was the inrush on the motor which was in the 50+ range that caused the tripping of the breaker. I may be wrong on this because the op said he was going to have it on a timer after he got this problem fixed. So either it was on a timer to start and stop or he was manually controlling it by the plug.