Hello,
I am reviewing a plan for 240VAC double pole 40A circuit, backed-up by two individual 120VAC On-line UPS's (one for each leg). Both of the UPS outputs tie back into a double pole 40A on the load side. My concern is if either of the UPS were to fail before the other, only 1 of 2 legs would be energized creating what seems to be a safety code violation, but which one?

Thanks,
JC
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Hello,
I am reviewing a plan for 240VAC double pole 40A circuit, backed-up by two individual 120VAC On-line UPS's (one for each leg). Both of the UPS outputs tie back into a double pole 40A on the load side. My concern is if either of the UPS were to fail before the other, only 1 of 2 legs would be energized creating what seems to be a safety code violation, but which one?

Thanks,
JC

Even before that I would ask whether the two UPS units are designed to be linked together (stacked) to produce 240V. If their outputs are not synchronized you cannot drive a 240V load.
 
Location
Virginia
GD~Thank you for the feedback (has helped me go further with the problem). The double pole breaker/ output from the combined (2) individual 120VAC UPS inverters, feeds a 120/240 LoadCenter containing only single pole circuits. This panel/ LC will not be outfitted with any double-pole circuits. So, I suppose the out-of-sync inverters will not cause any noticeable equipment operational issue for the 120v devices. Seems like this may only be an El Cheapo way of backing-up a system without the cost of a 240V UPS and since it will be maintained and accessible only by qualified personnel it may not pose a safety concern either.

Thanks again,

JC
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If there are only 120V loads and no circuits are wired as MWBC, you could also, in theory us NJe only
one double sized UPS. But that would require adding an external transfer switch instead of running just the UPS. And it would keep you from taking full advantage of a dual conversion UPS.
In any case, clearly mark the panel for no 240V loads, since it will appear to be an option to anyone who looks while the grid power is on.
 

jap

Senior Member
Occupation
Electrician
Hello,
I am reviewing a plan for 240VAC double pole 40A circuit, backed-up by two individual 120VAC On-line UPS's (one for each leg). Both of the UPS outputs tie back into a double pole 40A on the load side. My concern is if either of the UPS were to fail before the other, only 1 of 2 legs would be energized creating what seems to be a safety code violation, but which one?

Thanks,
JC

How are the output neutrals of the (2) separate UPS units connected to the load?


JAP>
 

iwire

Moderator
Staff member
Location
Massachusetts
In my opinion your plan results in a violation of NEC 110.3(B).

There is no way these units are designed to have the output neutrals combined or to feed a panel in this way.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In my opinion your plan results in a violation of NEC 110.3(B).

There is no way these units are designed to have the output neutrals combined or to feed a panel in this way.

I agree, but would it work? ;)
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I agree, but would it work? ;)

My guess would be no as many of these types of small UPS have circuitry to monitor basic wiring faults. But as others have said, I think this is a horrible idea even if it functioned. It brings to mind a whole host of NEC and NRTL issues.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I agree, but would it work? ;)
I seriously doubt it. I do not believe that the inverters in the UPS units would have any way of synchronizing with each other. The phase angle between their voltage waveforms would be completely random and their relative frequencies would probably drift.
 

iwire

Moderator
Staff member
Location
Massachusetts
I seriously doubt it. I do not believe that the inverters in the UPS units would have any way of synchronizing with each other. The phase angle between their voltage waveforms would be completely random and their relative frequencies would probably drift.

There are no 240 volt loads, only 120 volt so the lack of sync would not be an issue.
 