Voltage drop
I'm a bit hung up on a question , I need some guidance as to where & how I can solve it.
The voltage drop percentage for a panel feeder with a non-continuous load of 180A, using 3/0 THWN copper conductors at 480V, 3Ø, & a length of 248' is____
A.) 1.23%
B.) 1.28%
C.) 1.42%
D.) 2.03
A.) 1.23%
B.) 1.28%
C.) 1.42%
D.) 2.03
Single phase or three phase?
A.) 1.23%
B.) 1.28%
C.) 1.42%
D.) 2.03
Calculate the "effective round trip resistance" for the three phase line, by using R=L*r*sqrt(3)/1000. From there, it is simply the Ohm's law equation, with the phase-to-phase voltage and the per phase current. Then divide by the phase-to-phase voltage, and multiply by 100, to express it as a percent.
L is the one-way length
r is the ohms/1000 ft for the wire size & metal.
If you really want to get down to the difference between 1.23 and 1.28%, you will need a lot more information....power factor, raceway or cable type, and ambient temperature.
That being said, I expect that they have given you a formula that they expect you to use to get this answer. If you use that formula and the correct information, you will get the answer they want.
THE ANSWER TO YOU QUESTION IS 1.23%.