designer82
Senior Member
- Location
- Boston
When they tap a 3PH starter or circuit breaker for control power transformers or any other transformer for auxiliary loads, how do they actually make the bus tap? with a multi lug connector bolted to the bus?
I'm trying to tap this starter like shown. Have you seen this done? Maybe there's issues against doing this
I could even tap it ahead of the breaker and add another breaker, it doesn't matter.
Almost all combination starters are done that way. usually the tap is done on the line side of the starter (contactor) because they generally have lugs on them for doing this. 4160V though, that's a different story. Assuming that's a Draw-Out breaker, it likely has tap lugs available for the breaker terminals.
Thank you
That auxiliary tap would be a 75KVA transformer though with #1/0 conductors. Wouldn't be for control voltage, it would be for a pump motor for a chiller chilled water pump.