Eddie702
Licensed Electrician
- Western Massachusetts
- Electrician
I know that generally in accordance with the UL white book that 0-100 amps the wire termination temperature is assumed to be 60 deg C & 100 amps and up it is assumed to be 75 deg C If the equipment is not marked.
At least in my area service entrance conductors are usually sized at 75 C. When replacing an existing panel some or all of the older wiring (branch circuit & feeders) is 60 C wire.
I heard somewhere, that to use 75 C terminations and size the service entrance at 75C then all wiring in the panel (branch circuits & feeders, breakers etc.) must be rated 75 C. Is this true?? I don't see how it could be.
I have looked in the NEC and in my old "McGraw Hill handbook of electrical construction calculations" and haven't found a clear answer.
Thanks for the help!
Eddie 702
Eddie 702