Customer getting shocked by disposal switch

Status
Not open for further replies.
So I went on a service call about a month ago and the customer said they were getting shocked when they turned on the disposal. I couldn’t find anything wrong so I replaced the switch and said to call if it happens again. Well she called and said it’s happening again. Any thoughts?
 
That switch and plate should be all plastic. Only metal (that you could touch with plate on) would be the plate screws. Sounds like a static shock if anything. If you go back, I would suggest taking an extension cord and plugging it in to a receptacle that is not on the same circuit as the disposal. Take your meter and measure from the ground hole in the ext cord to the metal screws on the disposal switch. If you have much of any voltage there then you might investigate farther. I highly doubt the HO is getting a "true" shock just touching the switch.
This is assuming a normal switch w/plastic handle, and plastic cover plate.
 
How old is the house? What modifications have been made?
If it's older than c.1960 or so, check the plumbing. If there's a fault in the disposal and the house has plastic water pipe, the kitchen sink could be energized, which might result in a shock when touching it and a properly-wired, properly-grounded switch.
 
I'm sure you checked the wiring integrity first.

It may be an older disposal with internal insulation breakdown.
Some disposals have a supplemental ground screw that can be bonded under sink but replacement is advisable if it's the problem.
 
Most operate the disposal by turning on the water with one hand and toggling the switch at the same time with the other. Sometimes one hand is touching the basin, but either way they're essentially grounding themselves.
 
This is one of the few things non-contact voltage testers are really good at: finding random things which are unexpectedly electrified. The switch may not be the hot part.
 
This is one of the few things non-contact voltage testers are really good at: finding random things which are unexpectedly electrified. The switch may not be the hot part.

On the other hand, if you are holding the non contact tester and are coupled to an energized surface, the tester will alert for ground. :(
 