Conduit fill
wireday
New England
Master electrician
I would like to add a couple conductors to an existing 1/2 EMT run. The run currently has 2 #12 conductors and a #12 ground, 2 #10 conductors. I would like to add 2 more #12s, Im not sure of figuring the fill with two different size conductors.
Use table 4 and 5 from chapter 9 to do the calculation
12 THwn = .0133 sq. in
10 Thwn = .0211 sq.in
5x .0133 + 2 x .0211 = .0665 + .0422 = .1087 sq. in
Table 4 for emt shows 1/2" emt with over 2 wires(40%) at .122 sq.in
since .1087 is small than .122 then you are compliant. A long pull may not be so easy
Good catch. Since it is emt then you could just remove the equipment grounding conductor.
Would you be required to remove it? Why can't you use the #12 for the circuit with the #12 conductors and use the EMT for the #10's circuit?
Trevor I don't know why but I believe it is not compliant. There does not seem to be another option but IMO, there should be
250.122(C) Multiple Circuits. Where a single equipment grounding
conductor is run with multiple circuits in the same raceway,
cable, or cable tray, it shall be sized for the largest overcurrent
device protecting conductors in the raceway, cable, or cable
tray. Equipment grounding conductors installed in cable trays
shall meet the minimum requirements of 392.10(B)(1)(c).
I don't see 250.122(C) as precluding using the EMT as the EGC for one circuit and using the wire type EGC for the other circuit(s). That would be multiple EGCs, so 250.122(C) doesn't apply.
Cheers, Wayne
Actually wouldn't you be using the #12 and the conduit as the EGC for both circuits? I'm sure you have the #12 bonded to the boxes at both ends which puts the #12 and the conduit in parallel.
Like was said, you really don't need to use an separate EGC here at all, but many of us do because you don't want to rely just on the conduit. Though there is no reason not to, it's a matter of choice. So you are going to have to make up your mind. If you want a separate EGC I would remove the #12 and replace it with a #10 because a separate EGC says you aren't relying on the conduit. But if doing so exceeds the allowable fill then just remove the #12. Will make pulling easier anyway.
-Hal
Do they still make that stuff? Anyone still use it?
Yes, they still make it and some guys still use it.
I just talked with the boss about 77 the other day. He still loves it, says it's the best for a long hard pull. I've had better luck with Aqua Gel and it is much easier to clean up. 77 looks like puke & is hard to clean up. It gunks pipe up too & makes future removal of wire much harder.
-Hal
I would use the green as a pull wire for my new conductors.